There are a few jurisdictions that require GFCI protection of just about everything in the bathroom, but it's not in NEC.
However, NEC requires that the circuit feeding the GFCI in the bathroom have that as its only load. You can feed more than 1 bathroom GFCI from a single circuit, but not the lights, fan or other loads.
Check out 210.11(C)(3).