Jim,
If you are working under a very strict reading of the '96 code that would be a violation. Look at 110-16(a). It said: "...Equipment of equal depth shall be permitted within the height requirements of this section". In areas with very strict enforcement, contractors were required to build racks to make the fronts of the equipment flush with each other if they were within the work space."
This was never the real intent of the code section and it was revised in the '99 code. In the 99 code look at 110-26(a)(3).
"...Within the height requirements of this section, other equipment associated with the electrical installation located above or below the electrical equipment shall be permitted to extend not more than 6 in. (153 mm) beyond the front of the electrical equipment." So as long as it is electrical equipment and there is 6" or less difference in depth, it is ok with the NEC.
Don(resqcapt19)