All that spec seems to ad to 'standard practices' is that the EMT fittings need to have the plastic liners in their throats.

RMC, IMC need bushinge everwhere except threaded hubs.

Overall, the spec is no more onerous than ones calling for steel fittings (as opposed to zinc).

Oh- and watch that you use steel locknuts- and not zinc ones!