230.70(A)(1) "The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of enterance of the service conductors."

If your meter is remote, then I believe you'll need the service disconnect remote also. You can pedestal equipment that will hold your meter and main disconnect in one unit.

Why does the meter have to be 200 feet away anyway? If you move it to the building you'd ba OK.