"The 4 inch conduit needs to be reused"

May be time to find a new engineer for this job, sounds like he thinks he can save some bucks by trying to resuse the conduit, we usually never bid a job like that, with the intention that the conduit can be reused, usually what you find even if you can pull the feeders, is damaged conduit, not much good for pulling new feeders, shorter runs smaller feeders, you may have some luck, when you dig up the existing run, you will most likely find, either crimped conduit or a shift in the run near a coulping, or bend.

Just wondering, what did the old feeders meg out at?