Steve,
Quote
And NOT trip for "normal" arcing, like arcing when a switch is switched,
They don't trip for switching because they don't look at that type of arc. They only look at parallel arcing faults...faults from hot to neutral. They will trip on a ground fault because of the GFP protection. They may trip on a poor connection (series fault) if the fault progresses to a parallel arcing fault or to a ground fault...but will they do this before or after the fire starts.
Don


Don(resqcapt19)