Recently graduated from a VFD school.Never meg a VFD.Use polarization index using 1000volts for 480volt motors.Divide your ten minute reading by your one minute reading with the minimum result being 2,This is detailed in IEEE standard #43.If you get an immediate infinity ,giga ohms or tetra ohms it don't get no better!!Always meg motor isolated from VFD as not to destroy electronics.