Ditto Reno - take the Wye if you happen to have a choice, but in my experience, the poco is going to tell you what you'll be getting, and you design accordingly.
(Qty. 2) 1Ø transformers wired into an Open Delta will give 20A @ 120V or 10A @ 240V 3Ø
Small point of clarification here - open deltas are pretty much the same as a closed delta except they need to be derated to 67% of nameplate value because of the missing transformer.
Radar
There are 10 types of people. Those who know binary, and those who don't.