Oh, Ron, 8-10' 4X4 gutter, cut-in boxes for the outlets with an angle grinder, pipe into the end and mount top with a 'T' strut fitting, screw the bottom right to the floor. (Or if subject to wash down, put it on a post of strut above the floor.) You can run the conductors right through the gutter, and put them through a bushing into the cut-in boxes. An EGC is not a bad idea if going through pre-made KO's...

Might work for you too Highground, if it weren't for the stainless....