So you have about 410' to the MDP....
A #6, 240V run @25A will see 5% around 565'
A #8 , 240V,run @25 Amps will see a 5% drop at about 355'
A #10, 240V run @ 25A will see 5% at 230'
So in reality, Sub #2 is about at that length from source and that's all sub#2 can run as it is.
You could calculate the circuit as a splice, 210' of #10, then 200' of #6 , and probably make out ok. But it would seem simpler to make your run to the MDP.
I'm just going to the MDP, not the utility here.
Hope this doesn't bum you out..