Voltage drop doesn't care if it is coming or going, they add. You should make the neutral the same size as the ungrounded conductor. It might be argued that in a multiwire the neutral would not need to be any bigger than the 240.4(D) requirement since if the load was balanced it would not carry any current at all. If this is just a single circuit it carries the same as the ungrounded wire.