Well this is very interesting. The only reason I could see for the inspectors reason would be if you were running from a disconnect to a main lug panel, you would use ser. But you're not. Even if the panel is too far away from the entrance, I think you would be required to install a disconnect before the panel, not simply run ser instead of seu. I don't get it.