Yes it does have the 6 breakers on top all 240 volt with one 60a feeding the lower buss. So that serves as the 6 breaker disconnect rule? You still cannot shut down the whole panel at once, which seems to be code.

winnie, I installed a 400 amp panel a few years ago feeding a 100a from that. If I remember right, the 400a had 2-200a mains feeding a split buss. So that would take 2 mains to shut down the panel.
Art 408.16 does seem to say you cannot have more than 2 disconnects.