This should indicate that the terminal is listed for use at either temperature ampacity. If the teminal was only listed for use with a 60 degree termination it would affect the wire size you could use to achieve the required ampacity. See Section 310-10 and the associated Tables to see the affect of the different ampacities in the different temperature columms.