Note 4 Branch-Circuit Load. It shall be permissible to calculate the branch-circuit load for one range in accordance with Table 220.55. The branch-circuit load for one wall-mounted oven or one counter-mounted cooking unit shall be the nameplate rating of the appliance. The branch-circuit load for a counter-mounted cooking unit and not more than two wall-mounted ovens, all supplied from a single branch circuit and located in the same room, shall be calculated by adding the nameplate rating of the individual appliances and treating this total as equivalent to one range.

5.5+5.5+4= 15
15 ā€“ 12 = 3
3 X 5% = 15%
Demand in column ā€œCā€ is 8, 8 X 115% = 9.2
The demand for these three cooking appliances will be 9,200va


Mike