i will agree with Hotline1 with this sisuation.
to change over from 240 to 480 volts system it will take more than simple set up.
have to set up with 480 volts breaker [ they cost more than 240 v breakers are]
change wire circuits to reacmmuated with 480 volts [ some circuits can use the same wire but i will not recomned at all]
add a step down transformer for 120 volt plugs and 120 volts lighing circuits and some 240 or 208 v [ single or 3 phase ]
the electrical load the poco will figured out for correct size transformer by load demand usage not the main breaker rating unless hevey loaded
on most machinines when you change over to 480 volt the mmagatic starter or contractor have to change and the same thing with heater strips for overloads , motor reconnection etc etc
so there are some condersation you have to take a look at it not only on electrical side but the machery also for how much time to take to change over alot of items to work on proper votage
Merci , Marc