Couple of comments techie.
Yeah the hinge side of a door is a bad choice, raising the horn strobe to clear the door is a usually violation of the height.
The visual devices need to be around 82" AFF I can not remember the exact measurement.
The pull stations need to be within 5' of the door, many times that ends up with some pretty ugly installations on door mullions.
I can only speak for this area but once I have stamped approved prints from the FD I can not move devices. They go where shown...insane or not.