I have worked 12+ years in on site meter testing, calibration of electromechanical kWh meters and electronic ones. [Linked Image]

Running fast, not often but is due to the weakening of the brake magnet. Around 1998 we still took out in Devonport, Auckland NZ, Ferranti FDb meters and Chamberlain & Hookham 10 Amps LR meters which were last tested in 1926. These had an average error of around 7 % at 10 Amps Inom. Considering the normal peak house loads of 40 to 60 Amps + @ 230 Volts the meter would be on overload anyway and the current coil in saturation with a meter error of - 20%. I have proven that on a test bench.

A lot of current coils had shorted turns where the varnish and insulation had burnt of and the metal cased meter was live at mains potential. [Linked Image] [Linked Image]

On older meters the weakening of the brake magnet and the wearing out of the rotor bearings tend to cancel out each other a little.

The Floton bearing meters 1970's ( Sangamo series ) did not have any major problems at all except Jamming jumping dials. [Linked Image]

Most meters up to 50 years old are in general very accurate and overall errors are well wirhin the ±2½ % margin.

Some electronic meters do run fast, we had certain batches of meters around 1994 with capacitors on the circuitboards going faulty and the meter taking off. errors of 600% were found. This affected 1Ø and 3Ø meters. It was quite visible on the meterdial that the meter had a problem with hardly any load the led was blinking like crazy and the numbers of the dial rolling over. [Linked Image]:


The product of rotation, excitation and flux produces electricty.