If any individual phase of a three phase breaker exceeds the trip value (200A in your case), it trips all three together. So theoretically in a lab, you could draw 600A if your loads are phase to neutral and perfectly balanced.
Many leases include a cost for electricity based on square footage of the space occupied or a sub meter.


Ron