There is no length limit at all.

You can not have more than 360 degrees of bend. 350.26

It will have to be supported properly. 350.30

Longer than 6' and a grounding conductor will have to be run. 250.118


Bob Badger
Construction & Maintenance Electrician
Massachusetts