The conduit run in question is at the following stage of completion: On the street end it is not terminated at the pole yet because the original plan called for it to go to a pole roughly 800 feet from the building it served. The main entrance to the mall was redesigned making it necessary to remove this pole. The new target became a pole 300 plus feet away. They designed a concrete pull hole for the primary power, but none for the tel. or CATV. I have encouraged them to add these pull holes. Also, the 90 degree sweep at the pole will be rigid steel, as will the pole riser. The building end sits at the bottom of an excavated area inside the building awaiting completion by me early next week. When I do so, I will install a rigid steel 90 and stub thru the slab with steel.

Glad for the input here while I still had time to use it. Thanks and I'll keep you advised.

BTW, the cable guy was on site yesterday and said he just successfully pulled a 700 foot run on another job(not in 2" though).