#1 - How do you figure that #1 is technically correct? The interupting rating of a circuit breaker is measured in VOLTS!! I don't see how this can be correct in any way shape or form. "not what anyone in the trade would answer" - so who would give this as an answer??

#5 - I have no problem with this one, a bit tricky perhaps but I agree with the answer.

#9 - one of the answers is "Permanently Installed Pools". This is a better, i.e. more concise answer than "Pools" thus the answer key is wrong. It should be A not B.

#10 should be A "identified for standby use" not D "rated for continuous use". 702.4 makes no mention of a transfer switch being "rated for continuous use".