It will be bigger than you may need it if you size it to the breaker.
You could size it to the KW of the oven.
I am guessing you want 208 to become 240?
Using the 60 amp breaker and boosting 28 volts I come up with a 10 to 12 kVA transformer.
I got that from this chart.