Also: "250.66 Size of Alternating-Current Grounding Electrode
Conductor. The size of the grounding electrode conductor of a grounded or ungrounded ac system shall not be less than given in Table 250.66, except as permitted in 250.66(A) through (C).
FPN: See 250.24(B) for size of ac system conductor brought to service equipment.
(A) Connections to Rod, Pipe, or Plate Electrodes.
Where the grounding electrode conductor is connected to rod, pipe, or plate electrodes as permitted in 250.52(A)(5) or 250.52(A)(6), that portion of the conductor that is the sole connection to the grounding electrode shall not be required to be larger than 6 AWG copper wire or 4 AWG aluminum wire."