Mark you are correct it is basic ohms law lets take a look.

Lets say the circuit is 300 watts at 12 volts

300 watts / 12 volts = 25 amps

12 volts / 25 amps = 0.48 ohms

Now we know that the collection of lamps has a total resistance of 0.48 ohms

Now drop the voltage to 10 volts

10 volts / 0.48 ohms = 20.8 amps

Drop the voltage to 3 volts

3 volts / 0.48 ohms = 6.25 amps.

Drop the voltage all the way down to 1 volt

1 volt / 0.48 ohms = 2.08 amps

As far as the dimmers, I understand how a modern dimmer works, it does not matter the effect is the same.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts