Is not most THHN also listed THWN and vice versa?

I think you are correct. [Linked Image]

The reason many of us point out the need for a "W" type insulation is only to show off. [Linked Image] Well that and make everyone aware of 300.5(D)(5)

Quote
300.5(D)(5) Listing. Cables and insulated conductors installed in enclosures or raceways in underground installations shall be listed for use in wet locations.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts