The manufactures of modular furniture that I see often specify 15 amp OCPDs.
However I find most engineers are unaware of this or choose to ignore it.
OK I will give this a whirl
IMO you have 8 current carrying conductors.
310.15(B)(2)(c)On a 4-wire, 3-phase wye circuit where the major portion of the load consists of nonlinear loads, harmonic currents are present in the neutral conductor; the neutral shall therefore be considered a current-carrying conductor.
That is assuming the work stations have PCs, the pencil sharpeners, desk lamps etc. are just a small portion of the load.
I do not know of any NEC
requirement to up size the neutral although it makes good sense considering the furniture whip will probably have a 10 AWG grounded conductor? (For extra credit is it a grounded conductor before we connect it to the branch circuit or is just the white wire?
)
8
Current
Carring
Conductors, Table 310.15(B)(2)(a) shows a 70% for 7 - 9 CCCs
Table 310.16 shows 12 AWG Copper THHN rated at 30 amps.
30 x .7 = 21 amps
Table 310.16 shows 10 AWG Copper THHN rated at 40 amps.
40 x .7 = 28 amps
Seems both the 12 AWGs and the 10 AWGs are still rated high enough to use 20 amp breakers.
- Is this NEC compliant? Yes
- Will it work? Sure
- Is this a Design Issue? The use of 10 AWG for the grounded conductor was a design choice
- Does this example make sense? To me, yes, I deal with this exact situation often.
- Will the Penguin escape once again?
Probably......Batman is a major wuss Bob