Quote
In order to keep the 22 kAIC rating, you need to either use a 22 kAIC breaker feeding the subpanel (QOs series rate with other QOs, local or remote), or use only 22 kAIC breakers in the subpanel.

or couldn't you use a 10K AIC feeding a 22K AIC main breaker subpanel?