George.
IMO 250.34(A) and (B) allow any amount of equipment to be cord and plug connected to a generator without the use of a ground rod.
Part of 250.34
250.34 Portable and Vehicle-Mounted Generators.
(A) Portable Generators. The frame of a portable generator shall not be required to be grounded and shall be permitted to serve as the grounding electrode for a system supplied by the generator under the following conditions:
(1)The generator supplies only equipment mounted on the generator, cord-and-plug-connected equipment through receptacles mounted on the generator, or both,.....
I think it is important to notice
"cord-and-plug-connected equipment through receptacles mounted on the generator"They use the term "equipment" not the term "utilization equipment".
IMO this means you could feed a portable distribution panel to smaller panels and finally branch circuits
if it was all cord and plug connected.
What exactly is a ground rod going to do?
Bob