Originally posted by Redsy:
A 200 amp panel can handle 200 amps. However, this is not determined by adding up the breaker values.
Due to load diversity, it is very unlikely that each branch breaker will be loaded to its maximum value. As long as your calculated load does not exceed the panel rating, you are O.K. The same thing applies to Service Entrance conductors. A 200 amp service might, for practical resons, feed a 150 amp and 100 amp panel. As long as the calculated load does not exceed the Service Conductor rating.
Thank you for the info! This was what I figured. Thanks!