Be careful. What you may think is code may not be.
For example: I did a plan review for a commercial job with an 800 amp service. The engineer showed parrallel 500 KCMIL conductors, which would be allowed by the round up rule in 240.4. The problem is that the computed load was greater than 760 amps (parrallel 500's are worth 760). He didn't comply with 230.42, so I made him change it to 600's.
Now, what I am afraid of is that the contractor may be experienced with 800 amp services and has installed a lot of them with 500Kcmil conductors. If he does on this job he will be removing them
![[Linked Image]](https://www.electrical-contractor.net/ubb/frown.gif)
Be careful