Not my first choice either but give the customer what they want. [Linked Image]

If you end up doing this really look at the support requirements. Table 352.30(B)

1/2", 3/4" and 1" all require supports every 3 feet

Even 4" requires a support every 7 feet.

These supports "shall be fastened so that movement from thermal expansion or contraction is permitted." 352.30

This means do not use something like a EMT minni or a standard uni strut clip, you must use proper PVC supports that let the PVC slid through them.

Expansion fittings, plan on a lot of these.

IMO it is tough to make PVC look good over a long period of time.

Depending on building construction the support requirements could break the budget.

Say it is a steel truss building that has a 5' to 6' spacing, how will you support every 3'? eek: