Electric utility substations quite often have such a scheme. We normally have low side bank breakers at the output of the two transformers and a bus tie breaker between the buses. If either transformer fails its low side breaker is opened and the bus tie breaker is closed. There are interlocks to make sure that a failed transformer is not energized from the low side.