Please see Table 430-150. Full-Load Current Three-Phase Alternating-Current Motors
 The following values of full-load currents are typical for motors running at speeds usual for belted motors and motors with normal torque characteristics.
Motors built for low speeds (1200 rpm or less) or high torques may require more running current, and multispeed motors will have full-load current varying with speed. In these cases, the nameplate current rating shall be used.
The voltages listed are rated motor voltages. The currents listed shall be permitted for system voltage ranges of 110 to 120, 220 to 240, 440 to 480, and 550 to 600 volts.

Also, always use this table for FLC and refer to 430-6 in the 1999 NEC.

This has been the accepted practice for many years.


Joe Tedesco, NEC Consultant