Rob,
Yes, you are missing something. The rule in 110.3(B) only applies to instructions that are a part of the "listing and labeling" process. The instructions on the panel are "manufacturer's instructions and 110.3(B) does not require that you follow them. If 110.3(B) did apply to the manufacturer's instructions, then there would be no code compliant use for "classified" breakers.
Don