Don,

You are quoting NEC articles, but could it be that the NEC does not apply to generators of this type?

If the generator is isolated from ground and there is no ground connection at the outlet, there can be no leakage current.

If the neutral is bonded to the generator frame, then the ground terminal should also be bonded to the generator frame. If Honda has bonded the neutral but not the ground to the frame, I very much question the safety of this generator.