A "twin" breaker provides two (2) circuits from one (1) buss space; both at 120 volts to neutral. There is one (1) physical connection to the panel buss. They are also refered to as "piggybacks" and "tandem"

A common use of the above is to "add" additional circuit capacity to a "full" panel. The design intent was/is to provide a greater circuit capacity in a physically "smaller" cb panel. (See yoyr 20/20-24/4- post)

A "220" breaker, as you have referred to it, is a "two pole" breaker. It is basically two single pole, full size breakers with a common handle & trip. This breaker connects to two buss spaces, and provides 220 volts (or 240, or 208).

There are also some "twin" 2 pole breakers around, but that will really add to your confusion.

Hopefully this breif explanation helps you!
John


John