Hi RobbieD,
Welcome to the board.

Quote
This time I must install an exit sign and an emergency lighting unit seperately.{/quote]
Are these separate units or did you separate them? If you did, you shouldn't. It is listed as a complete unit.

If they are separate,[quote]next to the lighting unit for it to be plugged into with a cord
Typically, the units that I have worked with are not designed to be cord and plug connected.
Quote
My question is how do I supply the back-up power(6VDC) from the emergency light unit to the exit sign?

Your exit sign needs to have the circuitry for 6VDC which means it would already have it's own battery.

Does this help?
Dave



[This message has been edited by WebSparky (edited 02-23-2003).]


Dave