I have the same question as Mr Brown. Is this a backup and if so what does your transfer equipment look like? Does it switch the neutral? The generator is set up as an SDS so it will need a compliant ground electrode system. (probably 2 rods) As a practical question I doubt this is a safety issue as long as you have assured the generator really has the main bonding jumper installed and the GES in the building is good.