Trumpy, sorry for the late reply. As spring came, obviously my problems disappeared. Now, colder weather is coming way to soon and I need to revisit this problem again.
The power supply is a 120v GFCI receptacle in a weatherproof box with an "in-use" cover. The total load on the circuit is 13.7 amps.
Because the outside outlet is a convenience outlet, it is required to be of the 5MA variety of GFI protection.
My next course of action is to replace my single gang weatherproof box with a two gang weatherproof box, and add a second two gang weatherproof box next to it.
This will give me a total of four GFCI receptacles to plug into. Theoretically, this will allow me to plug no more than two heaters into any GFCI receptacle, thus keeping the leakage current well below the 5 MA trip threshold. I am also going to install a separate in-line GFI power unit on each pad. The pads are designed to only plug into either another pad or a GFI power unit.
Again, this should keep the leakage current well below the tripping level of the power unit.
I also intend on calling the manufacturer to find out what their maximum leakage current is. Should be an interesting conversation.