lastly, it does have taps but no guide.I was looking at the delta transfromer which also has taps but since the input voltage is greater that 468 (which was the 5% MARK) (V a-b 480, b-c 473, a-c 473), I did not venture into changing the taps on the wye transformer, I assumed that tap 4 would be for 468 input voltage and currently the transfromer it is set up for 100%(tap 3). I did not know how adversely changing thios to tap 4 would be for the output voltages. I figured that all the 240v would run fine down to 208 which is why I went high leg delta.

Last edited by mgawat; 08/05/19 05:41 PM.