Four Four inch from utility Transformer to CT Cabinet then to MCC. (XHHW).

three 600MCM & one 350 MCM each Conduit .

600 at 75C 420 amps x 4 = 1680 amp.

Very low Neutral load mostly 480 volt loads.

Using 310.15 (5) so no derating.

Engineer wants to use six six inch with four 400 mcm in each conduit.

I think conduit way over sized!