If it is installed outdoors, you can not install NM cable inside the EMT, it would have to be UF.
If a conduit is installed in a wet location, the interior of it is considered a wet location as well. NM cable is only suitable for normally dry locations per 334.10 (A)
BTW,
There are those who believe that NM cable installed in conduit is a violation of 334.40 which requires it to be secured within 12" of your boxes, etc. If the cable is in conduit, this requirement can not be met.