If they're powering something using the high leg that could be the problem. Single-phase loads can't be fed by the high leg and the neutral.
That voltage will read 208V on a meter but that's just a mathematical coincidence; you can't put any load on that or you're going to have nothing but trouble. All you have available to you with that type of system is 240V-3phase and 2 places that you can get 120V-1phase from.
Also, the total of the single phase loads is limited to 5% of the transformer rating or you'll start getting overheating problems in the transformer ahead of the Service.
Ghost307
|
|
|
Entire Thread
|
Contactors, 208v, 240v lighting questions.
|
Trick440
|
06/10/16 10:50 PM
|
Re: Contactors, 208v, 240v lighting questions.
|
HotLine1
|
06/11/16 01:50 AM
|
Re: Contactors, 208v, 240v lighting questions.
|
renosteinke
|
06/11/16 02:15 AM
|
Re: Contactors, 208v, 240v lighting questions.
|
Trick440
|
06/11/16 04:06 AM
|
Re: Contactors, 208v, 240v lighting questions.
|
Trick440
|
06/11/16 04:27 AM
|
Re: Contactors, 208v, 240v lighting questions.
|
NORCAL
|
06/11/16 07:02 AM
|
Re: Contactors, 208v, 240v lighting questions.
|
Trick440
|
06/11/16 03:55 PM
|
Re: Contactors, 208v, 240v lighting questions.
|
NORCAL
|
06/11/16 05:16 PM
|
Re: Contactors, 208v, 240v lighting questions.
|
HotLine1
|
06/12/16 04:39 AM
|
Re: Contactors, 208v, 240v lighting questions.
|
gfretwell
|
06/12/16 07:24 AM
|
Re: Contactors, 208v, 240v lighting questions.
|
renosteinke
|
06/12/16 02:12 PM
|
Re: Contactors, 208v, 240v lighting questions.
|
Trick440
|
06/13/16 11:03 PM
|
Re: Contactors, 208v, 240v lighting questions.
|
HotLine1
|
06/13/16 11:16 PM
|
Re: Contactors, 208v, 240v lighting questions.
|
HotLine1
|
06/13/16 11:29 PM
|
Re: Contactors, 208v, 240v lighting questions.
|
gfretwell
|
06/14/16 01:31 AM
|
Re: Contactors, 208v, 240v lighting questions.
|
HotLine1
|
06/14/16 08:16 PM
|
Re: Contactors, 208v, 240v lighting questions.
|
Trick440
|
06/14/16 08:17 PM
|
Re: Contactors, 208v, 240v lighting questions.
|
JBD
|
07/06/16 08:38 PM
|
Re: Contactors, 208v, 240v lighting questions.
|
HotLine1
|
06/14/16 08:44 PM
|
Re: Contactors, 208v, 240v lighting questions.
|
renosteinke
|
06/15/16 01:03 AM
|
Re: Contactors, 208v, 240v lighting questions.
|
HotLine1
|
06/15/16 02:33 AM
|
Re: Contactors, 208v, 240v lighting questions.
|
Trick440
|
06/16/16 06:00 AM
|
Re: Contactors, 208v, 240v lighting questions.
|
ghost307
|
06/16/16 01:28 PM
|
Re: Contactors, 208v, 240v lighting questions.
|
gfretwell
|
07/06/16 09:43 PM
|
Re: Contactors, 208v, 240v lighting questions.
|
wa2ise
|
07/08/16 07:06 PM
|
Re: Contactors, 208v, 240v lighting questions.
|
ghost307
|
07/08/16 07:23 PM
|
Re: Contactors, 208v, 240v lighting questions.
|
HotLine1
|
07/07/16 08:23 PM
|
Re: Contactors, 208v, 240v lighting questions.
|
gfretwell
|
07/08/16 07:28 PM
|
Re: Contactors, 208v, 240v lighting questions.
|
gfretwell
|
07/08/16 07:35 PM
|
|
Posts: 99
Joined: August 2003
|
|
|
|