Can you even put more then 3 Phase conductors + ground or Neutral in a single conduit?? I've never seen it Done???
HV ductbanks are derated by the number of conduits in the Ductbank not wires in the conduit.
Figure 310.60 Page 342 NFPA Code handbook.
70-159 NEC 2011