Your eyesight is going...

0.52 Amps would be a typical figure -- never 0.052.

"Max amps" means that you're charging up the battery while running the lamp. This is an interesting figure -- but irrelevant for circuit design. Such a surge, by definition, is an intermittent load.

Putting 28 EXITS on one circuit is only possible if the circuit is 277VAC... And that's really pushing it. I saw such a circuit in the Plans and Specifications for an Albertsons in the Bay Area.

It was converted, in the field, to three 120VAC circuits. None of the Albertsons supplied EM fixtures was able to tolerate 277VAC. While the electronic ballast could handle that voltage -- the battery system could not.

Due to mass production economics, it makes no sense to manufacture 277VAC battery packs for the itsy bitsy EM market -- when the 120VAC stuff is still flying off the shelf -- and 120VAC is ALWAYS available whenever 277VAC is the Service voltage.

Beyond that, any D-B scheme is not going to want EM circuits daisy-chained forever. You're going to suffer brutal voltage drops -- unless you're willing to insanely up-size your branch conductors.

EM fixtures are ALWAYS spread out. They are best served by dedicated circuits in most commercial settings. That way smart switching -- and overrides -- can be effected at the distribution panel/ lighting control circuit.

So, without even looking at the print, I'd say that a practical scheme is going to require three to four dedicated circuits. Another option is to have fewer circuits but branch them away/ split them for voltage drop the moment they leave the distribution panel. DON'T attempt to daisy-chain them on and on.

Examples: Perimeter lighting -- exterior facing illumination that wraps the building.

Plan A -- Branch circuit starts at panel and wraps the building from one direction -- clockwise. Voltage drop by the end is brutal. Pipe and wire up-sized to #10.

Plan B -- Branch circuit starts at panel -- then splits its load in half in a j-box / gutter right over the panel. One leg heads off clockwise -- the other heads off counter-clock wise. While both are tapping a single breaker, each #12 conductor sees only its half of the lumiere load.

Two half-wraps complete the perimeter illumination demand. Neither is required to up-size pipe or conductors.

%%%%

You need to go with Plan B ... with the EMs replacing the wrap logic/ layout expressed above.

&&&&

BTW, you should face max amps only once: at start. After the building burns down, it will face max amps a second time.



Tesla