Small jobs with a single panelboard can be subject to concern for SCCR of equipment. For example, a local coffee shop has a 150 KVA transformer located close to the building to provide 3phase 120/208 service to the building. The available fault current at the secondary of the transformer will be over 40K short circuit amps. Not all these jobs are engineered and the contractor must check to be sure his service equipment can handle the fault current.

Here is a link to some general information on SCCR...

http://www.cooperindustries.com/con...b_Short_Circuit_Current_Calculations.pdf