"I drive a ground rod run #6 to meter base this is the GEC correct? The GEC is run with circuit conductors"

The 'GEC' terminates at the neutral block in first means of disconnect of the service. Your POCO may allow it to be terminated within the meter base, but that is forbidden here by PSE&G.

The 'ground' with the circuit conductors is "EGC" for Equipment grounding conductor.


John