Test question?

My answer would be only materials directly associated with the elevator may be in the shaft plus the smoke detector.
From 38-005 the minimum headroom is 2000mm but that is for controllers, disconnecting means but not panelboards which I would prohibit under 6-206 locating a panel in a hoistway should anyone think it is an acceptable location.