Originally Posted by twh
I understand the CEC will have a table that shows 14 wire as being good for 25 amps, and a rule that the over-current can't exceed 15 amps. BEAT THAT FOR GOOFY, USA!


That's exactly what the 2011 NEC Table 310.15(B)(16) says as well as each previous version (disclaimer; the oldest NEC in my office is 1987).

Looks like you guys are finally coming around, eh?

The 25 amp value can be used for derating, but over-current protection remains at the 15 amp maximum regardless.